"Device Driver Call Failed"+Vacuum pump shuts off
The Vacuum pump shuts off and I get "Device Driver Call Failed" error on my Microrouter at random times, usually just when I am about to set my offsets
Last edited by bradders on Fri 17 Apr , 2009 11:01 am, edited 6 times in total.
Hi,
This is a problem I have seen over here. There is a similar post in the malaysia VIP area.
The problem we had was that the nextmove power was shutting down completely. Get the customer to look at the nextmove next time it happens and see if the 7 seg display is still lit.
In our case it was not. It seems the regulator on the bottom card of the nextmove can shut down if it is overtemperature, over voltage or current limits.
We disconnected all the orange connectors other than the power and the board still shutdown after 5 - 10 mins proving it to be a board fault rather than an output dragging down the supply.
If the 7 seg display goes out then change the Nextmove bottom card.
This is a problem I have seen over here. There is a similar post in the malaysia VIP area.
The problem we had was that the nextmove power was shutting down completely. Get the customer to look at the nextmove next time it happens and see if the 7 seg display is still lit.
In our case it was not. It seems the regulator on the bottom card of the nextmove can shut down if it is overtemperature, over voltage or current limits.
We disconnected all the orange connectors other than the power and the board still shutdown after 5 - 10 mins proving it to be a board fault rather than an output dragging down the supply.
If the 7 seg display goes out then change the Nextmove bottom card.